my ph fan is desigened to handle 100000 m3/hr @ 370 deg @ 250 kw shaft power @ 0.56 kg/m3 density @ 990 rpm @ 670 mmwg as per fan curve . now after putting WHR boiler in the system my fan inlet temp is 210 deg , now i use only 90% speed for the same production of kiln with WHR boiler . As per calculations volume will be 100000*0.9 m3/hr density will be 0.75 kg/m3 due to lower temp. pressure will be 670*0.75/0.56*0.9*0.9 & power should be 250 *0.9*0.9*0.9*0.75/0.56 kw I think the calculation is correct but in the operation i do not get such high pressure at the fan inlet . please comment about the calculations & reduced speed of fan for the same output ramesh